Hi C-Mach.
If that is the case then this is probably one of your machines

I finally got hold of Boema and found out they had supplied me with the wrong part (well, I guess I had asked for the wrong part, but if they had replied to my original email, that would not have happened). The 1d5 will control boiler water level but has no control over the main contactor so there is no protection for the element. What I needed was a 1d5e which does have a terminal for the contactor and therefore provides some protection for the element if the boiler runs dry.
Boema very kindly agreed to exchange the controller I had for the correct one and I have just finished installing the 1d5e this morning. I have pulled my first few shots which whilst ugly to begin with are starting to get better :P I have taken some photos and will do a brief write up of the install for posterity and any one else that may need the info in the future.
I now have a separate problem with the procon pump which weeps a little from the end with the round metal disc with procon written on it when the pump is running. Does anyone have a source for rebuild kits for procon pumps?
Thanks.
Paul.


) The unit arrived but the only documentation with it is a sticker on the side with a sort of a circuit diagram that isnt particularly helpful. It would appear that the unit supplied doesnt control the boiler water level and the main contactor as advertised in the Gicar PDF, however I could be wrong as the diagram on the unit is a little rudimentary.